7/4/2024 4:08 PM | |
Joined: 3/28/2010 Last visit: 7/6/2024 Posts: 1043 Rating:
|
The 6ES7134-6TD00-0CA module does not take a 4-20mA (HART) current signal directly (See page 16 for the input types). This module is really a universal temperature sensor card, designed for thermocouples and RTDs. It can take a DC volts input, and any current signal can be converted to a voltage input by creating an IR (voltage) drop across a resistor connected across the (+) and (-) analog input terminals. The module's maximum voltage input range (page 17) is ±1.0V DC. A precision 50 Ohm resistor will create a 0.20V to 1.00V dc drop over the range of 4-20mA. Notes 1. You'd have to scale the engineering units to account for the use of only 0.2-1.0 Volts on a -1.0V to +1.0V input. 2. The 0.2 to 1.0 V span uses only 40% of the module's ±1.0V resolution, so you're losing 60% of module's resolution. 3. HART communications will not function with a 50 Ohm input resistor because HART needs a minimum of 230 Ohms of loop resistance to operate. If you to add a 250 Ohm resistor in another part of current loop (not across the (+) and (-) terminals), then HART would operate. Manual: https://cache.industry.siemens.com/dl/files/600/59753600/att_71712/v1/et200sp_ai_4xrtd_tc_2_3_4_wire_hf_manual_en-US_en-US.pdf Attachmentet200sp_ai_4xrtd_tc_2_3_4_wire_hf_manual_en-US_en-US.pdf (1 Downloads) |
Last edited by: Wit_Moderator at: 07/05/2024 13:32:07File attached from link |
|
7/6/2024 11:42 AM | |
Joined: 7/28/2023 Last visit: 7/6/2024 Posts: 6 Rating:
|
Hi , My card is 6ES7134-6TD00-0CA1 and not 6ES7134-6JD00-0CA1 Any suggestions on my queries please |