1/2/2018 5:27 PM | |
Joined: 10/13/2012 Last visit: 8/16/2024 Posts: 79 Rating: (0) |
Alarms:- 1. alarm no 300504 measuring circuit error motor measuring system 2. alarm no 300505 measuring circuit error absolute track 3. alarm no 300509 converter frequency exceeded 4. alarm no 26020 encoder 1 hardware fault 00101000H how to solve this problems please help me its coming two axis please check attachment ------------------------------------------------------------------------------------------ |
Last edited by: CS Moderator at: 1/3/2018 2:30:00 PMNew subject after splitting |
|
1/4/2018 5:33 AM | |
Joined: 10/17/2007 Last visit: 10/17/2024 Posts: 4047 Rating: (355)
|
No story for m/c history, running good last night? have error this morning? normally no possible 2 axis encoders or cable have problem at the same time? but from alarm it is very like motor encoder cable not connected or cut off some where. if not fining , replace 611D control card 1st (if no spare , try to find possible same control card type to switch)
|
If you like my comments please |
|
1/5/2018 2:22 PM | |
Joined: 10/13/2012 Last visit: 8/16/2024 Posts: 79 Rating: (0) |
servo motor encoder has found as burned ... totally 3 axis motor encoder burned , what was the reason can't found , |
3/19/2018 2:05 PM | |
Joined: 6/19/2017 Last visit: 9/6/2024 Posts: 8175 Rating: (172) |
New question published by AutoGen_670438 is split to a separate thread with the subject How make diference between encoder 1 or 2 when have linear scale?. Best regards |