Hello, maybe for start, without to see what you set there and screenshots from your cfg/code, hard to help. Can you also pls give some documentation link/page where to see parameteres? Then maybe someone can give you tips. ZIP screenshots. Update: generally, this is help with telegram 111 as example (never tested by me): Controlling V90 PN |
Last edited by: Duris_I at: 04/29/2021 13:14:12Last edited by: Duris_I at: 04/29/2021 13:24:03Last edited by: Jen_Moderator at: 04/29/2021 13:51:16Optimized link. With best regards... |
|
4/29/2021 2:19 PM | |
Posts: 4 Rating: (0) |
Hello, I took some screenshots of my config. I can turn on/off the drive and set pos mode by writing the control words in DB, but I can't set MDI. I have used this manual for reference: V90 manual Thank you AttachmentTIAScreenshot.zip (523 Downloads) |
Last edited by: Jen_Moderator at: 04/30/2021 07:24:00Optimized link. |
|
4/29/2021 3:16 PM | |
Joined: 4/28/2015 Last visit: 10/22/2024 Posts: 1278 Rating: (300) |
Hi, I can just recommend the DriveLib which has integrated the FB283 for S7-300 PLCs in TIA Portal. With that FB you can handle the cyclic and acyclic data exchange to the EPOS function in the drive. https://support.industry.siemens.com/cs/de/en/view/109475044 |