5/8/2024 11:37 AM | |
Joined: 8/3/2009 Last visit: 11/8/2024 Posts: 14127 Rating: (1769)
|
Hello ngongpro Unfortunately for WinCC Advanced RT in Runtime are only 8 parallel OPC UA Connections released: https://support.industry.siemens.com/cs/ww/en/view/109815056/149330105483 So you can create 16 but there will propably not work all 16 you can use a higher HMI like WinCC Prof or WinCC V8 for more connections or use a datacollector PLC or you use an OPC Server in between for collecting the Items Bye Murof |
Last edited by: Murof at: 05/08/2024 11:37:56If this Information really helps, you could use the Rate function |
|