9/17/2009 6:11 AM | |
Posts: 139 Rating: (25) |
G'Day aswell as enabling the no load voltage diagnostic you will also have to go the address tab and enable the status byte which will will be updated in your normal I/O process image. The no load voltage bit to check will be bit 3 of the status byte. For more information see page 28 of the system manual http://support.automation.siemens.com/WW/view/en/1144348 alternatively if you donty want to use the status byte and evaluate only when there is a problem then you can use the variables in thetemporary memory of OB82 which will be called in the event of loss of power to the module, (or other I/O card fault). |
9/17/2009 12:02 PM | |
Posts: 66 Rating: (0) |
Hello Anchobi, Thanks this is clear. Can you tell me how to read out this 2043 addres see *.jpg. Thank you very much J. Timmermans |
9/17/2009 1:13 PM | |
Posts: 66 Rating: (0) |
Hello Anchobi, I am using a ET200s module see project zip. I 'don't get the same Addresses tab as your printscreen. This project is only to test at the office (test_saf) , the real project will include also ET200pro. These "PM-E modules" have the exact same properties as the ET200s. Thanks J. Timmermans AttachmentTest_saf_090917a.zip (163 Downloads) |
Last edited by: timmermans at: 9/17/2009 1:15 PM |
|
9/17/2009 1:16 PM | |
Posts: 66 Rating: (0) |
the real project.
Attachmenttest.zip (173 Downloads) |