Hello k.k the IM151-8 PN/DP CPU can be a Profinet I/O Controller, Profinet I/O device (aka Profinet I-Slave) or Profibus DP Master but can NOT be a Profibus DP Slave (you'd need theIM151-7 CPU for that). What you can do though is this: Add the Profibus DP Master module (6ES7138-4HA00-0AB0) to your IM151-8. Link it to a DP/DP coupler (6ES7 158-0AD01-0XA0) Link the other side of your DP/DP coupler to your S7-400 H system viaa Y-Link. I hope this helps |