I want to back up the Sinumerik M GA3 (milling machine). I have all the necessary files but I can't transfer them (I use PCIN) on channel 1. The person who did the backup many years ago told me to try on channel 2 because channel 1 is for transferring work programs. I set bits 5019 and 5021 to 11000111 and 5024 to 00101000, but the channel change like 2 RTS LINE and 1 RTS LINE does not appear on the display. What is the bit line and what configuration does it have for this change? Thanks in advance for your help! ------------------------------------------------------------------------------------------ |
Last edited by: The Helping Hand at: 03/06/2024 10:22:27New subject after splitting and text formatting optimized Last edited by: The Helping Hand at: 03/07/2024 07:57:04Headline optimized |
|
3/7/2024 3:07 AM | |
Joined: 10/17/2007 Last visit: 10/17/2024 Posts: 4047 Rating: (355)
|
we need make something clear , so we can work on the same page. #1--Data Back up and Data reload/restore --when we say back up , we transfer data from CNC RAM thru SW (PCIN) to the external PC saving to the HDD in PC. oppositely we call transfer back-uped data to from PC to CNC RAM, we call reload or data restore #2--on the 810M or 820M, when use transfer com (RS232) port, we don't call the channel 1 or 2, we call them interface-1 and interface-2, . Do you know in 810M there are 2 CNC channels, and channel-1 and channel-2 can run separate NC programs at the same time. so please use interface-1, and change setting data 5010,5011,5016 and so on, you can take picture or write down the original value of above setting data, when you job done, write them back. you can follow here Need to reload 810t with plc files and data etc., which you see I answered them
|
Last edited by: nulizhang at: 03/07/2024 03:15:24If you like my comments please |
|
This contribution was helpful to1 thankful Users |
Follow us on