Dear Mr. Raeymaekers, To assure the permanent function of only a single ET200M at the redundant system you would need to apply the Y-Link. The description of the configuration can be found under: http://support.automation.siemens.com/WW/view/en/6847578 New: Y Link to Connect Single-Channel DP Slaves to S7-400H Best regards Technical Customer Support A&D AS CS1 |