6/18/2009 3:45 PM | |
Joined: 9/27/2007 Last visit: 12/18/2020 Posts: 993 Rating: (102)
|
Hi Noboby can give you an answer. A PCS7 System can have a lot of komponents (PLS, OS, devices,...). the mosttolerate a litle bitdifferent ranges. You have to specify this questions. For all prdoucts exsists the rigth power supply modul or component. In which context, you have to answer this question??? regards cumulus |
Last edited by: cumulus at: 6/18/2009 3:48 PMLearn more about visualization - visit the HMI courses of Siemens AG! |
|
6/18/2009 4:00 PM | |
Joined: 9/27/2006 Last visit: 7/26/2024 Posts: 12270 Rating: (2676) |
Hello prataks; If you are speaking of S7-400 CPUs used for PCS 7, you coulduse the Power supply modules chapter from the S7-400 Module Data manual to locate the information you request: http://support.automation.siemens.com/WW/view/en/1117740 You will find specifications for each power module MLFB, such as: Specifications of the PS 407 10A and the PS 407 10A R Input voltage • Rated value 110/230 V DC 20/230 V AC (varying voltage input) Line frequency • Rated value 50/60 Hz • Permissible range 47 to 63 Hz |
6/19/2009 7:59 AM | |
Posts: 130 Rating: (18) |
Thank you for your comments. regards, |
Follow us on