3/11/2009 4:26 AM | |
Posts: 92 Rating: (7) |
dear chutia, please use a serial cable, please find the cable connections in the attachment.(use 9pin both side) connect the cable to 9-pin rs232 port on pcu20 or pcu50 (which ever you have), this is com port 2 for the controller. here is the procedure :- 1. select menu button. 2. now select start up. 3. set the pass word to higher level. 4. select menu button. 5. select services soft key. 6. now select the soft key "INTERFACE OR SET" - the right most softkey. here set the parameters for data transfer. com port : 2 (as using 9 -pin connector) baud rate : 19200 parity : none. data bits : 8 stop bits: 1. format: binary (start up data) text (part program, sub programs) 7. select ok. 8. if you need to transfer data into control, select data in other wise data out. 9.on computer open winpcin, select the correct com port on your com port. 10. set the baud rate and other settings similar to the control settings. 11. select recieve data to recieve data from control other wise send data. 12. after this select rs232 -- start soft key on the controller. now data can be transfered...... Attachmentrs232 pin.pdf (2353 Downloads) |
This contribution was helpful to3 thankful Users |
2/27/2017 3:52 PM | |
Joined: 9/3/2014 Last visit: 3/13/2019 Posts: 4766 Rating: (122) |
New question published by armenia1979 is split to a separate thread with the subject Sinumeric 810 ownloading /uploading parameters with winpcin. Best regards |