6/2/2020 8:36 AM | |
Joined: 12/18/2014 Last visit: 9/15/2025 Posts: 35962 Rating:
|
Please, can you make also photos of B-STACK and I-STACK? |
6/2/2020 8:39 AM | |
Joined: 3/5/2019 Last visit: 4/6/2022 Posts: 9 Rating:
|
Thanks for reply - I will But it will be tomorrow morning if the fault is there again |
6/3/2020 8:29 AM | |
Joined: 3/5/2019 Last visit: 4/6/2022 Posts: 9 Rating:
|
This morning the CPU was still in run. The difference from yesterday is that the OP panel is not connected |
6/4/2020 7:36 AM | |
Joined: 3/5/2019 Last visit: 4/6/2022 Posts: 9 Rating:
|
|
6/4/2020 7:53 AM | |
Joined: 12/18/2014 Last visit: 9/15/2025 Posts: 35962 Rating:
|
An extract from the manual is attached.
AttachmentS5-100U Manual page 90.pdf (529 Downloads) |
This contribution was helpful to
1 thankful Users |
6/12/2020 8:54 AM | |
Joined: 3/5/2019 Last visit: 4/6/2022 Posts: 9 Rating:
|
It has been working well for 6 days now after we changed the battery. So maybe that was causing the problem? |
Follow us on