12/12/2020 5:02 AM | |
Joined: 12/18/2014 Last visit: 9/15/2025 Posts: 35961 Rating:
|
The expansion modules of the 0BA8 series (6ED1055-XXXXX-0BA2) can be combined with each 0BA8 base module and with each other. Exception 1: Digital 24 VDC expansion modules cannot be combined directly with 230 VAC base or expansion modules. An analog expansion module must be connected in between for electrical isolation. Exception 2: No 230 VAC expansion modules may be added to digital 24 VDC expansion modules or analog expansion modules.
AttachmentLOGO! 8 manual 0BA8 2014_06 pages 30+31.pdf (330 Downloads) |
This contribution was helpful to
1 thankful Users |
12/12/2020 9:31 AM | |
Joined: 12/11/2020 Last visit: 11/27/2022 Posts: 2 Rating:
|
Thanks for the underline in the manual |
This contribution was helpful to
1 thankful Users |