2/22/2023 5:18 PM | |
Joined: 4/9/2021 Last visit: 2/22/2023 Posts: 4 Rating:
|
Question, do the M terminals have to be jumpered externally? Can I jumper all M terminals of the outputs? Attached you can see the image of my question. Regards ! ------------------------------------------------------------------------------------------ |
Last edited by: simoncostantino at: 02/22/2023 17:21:04Last edited by: Jen_Moderator at: 02/23/2023 04:49:47New subject after splitting |
|
2/22/2023 5:21 PM | |
Joined: 12/18/2014 Last visit: 9/5/2025 Posts: 35928 Rating:
|
I think all terminals named "M" are intern connected. |
2/22/2023 5:37 PM | |
Joined: 4/9/2021 Last visit: 2/22/2023 Posts: 4 Rating:
|
I measured it with the multimeter and they are not connected internally. |
2/22/2023 5:42 PM | |
Joined: 12/18/2014 Last visit: 9/5/2025 Posts: 35928 Rating:
|
Then tell me: How can this work what Siemens says in the manual? |
2/22/2023 6:52 PM | |
Joined: 12/18/2014 Last visit: 9/5/2025 Posts: 35928 Rating:
|
I don't know what else to write to you. Siemens could have drawn this for 4 loads, the result would be the same. You probably put the test probes of your measuring device on the terminals on the LOGO! without putting them under the terminals and without screwing the terminals tight. This leads to incorrect measurements. But: You can ask Siemens directly about this via a Support Request. |
2/22/2023 9:02 PM | |
Joined: 6/11/2019 Last visit: 9/5/2025 Posts: 2627 Rating:
|
With a Logo with a transistor output (CE), all outputs marked with "M" are also connected to the "M" of the power supply. This was also a topic in the german part of the forum. However, the first image has an error.The relays and indicator lights are not connected together to X2 24V. The "Qx" outputs deliver the voltage of 24V compared to "M". This means that the connection you marked in red in the second picture is possible. Ella_68 (translated with Google) |
Follow us on