7/25/2025 4:51 PM | |
Joined: 4/28/2015 Last visit: 8/28/2025 Posts: 68 Rating:
|
I suggest you use the “measure” bit in the tool status, which is $TC_TP8. This link should go to the section in the Tool Management document that covers tool data. https://support.industry.siemens.com/cs/ww/en/view/109801248/143923174411 You need the internal tool number as an index. For the current active tool, this is $P_TOOLNO. You can use B_AND and B_OR to check and set the measure bit as needed. HTH |
This contribution was helpful to
1 thankful Users |
7/25/2025 5:54 PM | |
Joined: 10/17/2007 Last visit: 9/2/2025 Posts: 4423 Rating:
|
Very good and professional answer , Steve, I don't know, for Neil is it too complex to deal with system variables and logical operations . so I suggest him to contact OEM, or using Programming Guide Advanced, here i can attach Tool Management Doc
AttachmentFBWsl_1015_en_en-US.pdf (51 Downloads) |
Last edited by: nulizhang at: 07/25/2025 18:00:04If you like my comments please |
|