hello and what type of regulation do you have |
10/3/2023 1:02 PM | |
Posts: 12 Rating:
|
Hello, Thank you for your feedback. I am not the developper of the system, I am just a user. How can I know which type of regulation is used ? Best regards |
10/4/2023 8:38 AM | |
Posts: 12 Rating:
|
Hi, P100 = 1 V/Hz and I find r490 (torque setpoint) = 0 you can find attached the drive's reference. Best regards. |
10/6/2023 7:46 AM | |
Posts: 12 Rating:
|
hello, any update please ? |
Last edited by: Bilel munich at: 10/06/2023 07:46:30 |
|
10/6/2023 8:31 AM | |
Joined: 9/23/2005 Last visit: 9/12/2025 Posts: 5116 Rating:
|
Yes, this is normal. In V/f mode (as P100 = 1), torque setpoint is 0. Get this - more than you ever wanted to know about Simovert VC. |
Regards, |
|
This contribution was helpful to
1 thankful Users |
10/6/2023 10:07 AM | |
Posts: 12 Rating:
|
Hello, I used the trace function and I have obtain that (find excel file attached). I find this very weird that the current change value but the torque is always nul. I cannot understand how we have a motor running and a torque = 0. Best regards AttachmentCourbe_masterdrive.xlsx (473 Downloads) |