2/27/2015 12:09 PM | |
Posts: 3093 Rating: (323)
|
Hello Tylim, In the variable table you use the display format DEZ the range is from - 32768 to +32767 - in HEX it is form 0000 to FFFF. Your remark to the address mapping: just have a look at the picture on the following page of the manual, then it will be easier to understand. After changing the data mapping a STOP/RUN transition of the CPU us required.
For general understanding of Modbus Smiffy posted a great compendium: Regards, |
2/27/2015 1:03 PM | |
Joined: 9/22/2014 Last visit: 8/17/2015 Posts: 96 Rating: (0) |
hi, i did change the single_write to true but however i still got the error A006 thank for document, btw can we use code 16 as code 6 because it seem like code 16 can do what code 6 can |