6/2/2022 11:43 AM | |
Joined: 4/8/2021 Last visit: 10/31/2024 Posts: 639 Rating: (107) |
Hi, Generally, in the case of Modbus TCP communication, Modbus TCP server is addressed via its IP address so MB_UNIT_ID is not relevant. However, as indicated in the post above and in the following section of the manual, sometimes the modbus server requires a specific MB_UNIT_ID so it may be your case. https://support.industry.siemens.com/cs/ww/en/view/109798671/141152652171 Therefore i would check the documentation of your Modbus TCP server to check it. Hope it helps. Br, Cocolino |
Best regards, |
|