Hi Oualid Babaaissa, Did you set the X51 as the storage medium for your parameter set type? The alarms you mentioned indicate that the storage medium in the X51 interface is unavailable. They also indicate that the Parameter Control service is not connected to its storage. Therefore, make sure the storage medium is available. Even if it is available, removing and replugging the medium may trigger the mounting service and resolve the alarm issue. I honestly do not know if the Parameter Control service will attempt to connect to the storage cyclically. Restarting the runtime ensures that all processes restart as well. Kind regards |