Joined: 4/28/2009 Last visit: 9/16/2024 Posts: 347 Rating: (43) |
Hello, only G130 CU320-2 PN is supported by Startdrive V17. For details see https://support.industry.siemens.com/cs/cz/en/view/109761180. You can have CU320-2 DP in Startdrive V17 only as field device. You can configure address, telegram, but you can't commision it in Startdrive. CU320-2 DP object is in Other field devices in Hardware catalog. With regards Martin |
Last edited by: Martin472 at: 07/22/2022 14:12:06Last edited by: Martin472 at: 07/22/2022 14:12:52Last edited by: Martin472 at: 07/26/2022 08:31:43 |
|
7/26/2022 1:40 PM | |
Joined: 2/12/2018 Last visit: 7/27/2022 Posts: 2 Rating: (0) |
Hi Thanks for taking the time to reply. I told them we need to migrate to profinet but no Thanks for the help. Regards |
8/2/2022 11:45 AM | |
Joined: 4/28/2015 Last visit: 10/22/2024 Posts: 1278 Rating: (300) |
Hi, now the Startdrive V17 SP1 is available and it supports PROFIBUS for G130. https://support.industry.siemens.com/cs/de/en/view/109812009 |