Joined: 8/3/2009 Last visit: 9/12/2025 Posts: 16409 Rating:
|
Hello nazmy91 perhaps some information from this FAQ could help: https://support.industry.siemens.com/cs/de/en/view/68202723 Bye Murof |
If this Information really helps, you could use the Rate function |
|
5/20/2025 8:53 PM | |
Joined: 4/27/2025 Last visit: 8/14/2025 Posts: 4 Rating:
|
Thank you for your reply; I really appreciate it. I used the same program after making some changes for my different setup, but it still doesn't work. I've attached a file that describes the problem with a simple program, but I always encounter an error. I've never succeeded in getting the TX and RX to blink or receiving a confirmation from the send P2P. I also tested the slave with a Modbus poll, and it works. I've tried everything, so please check the file and let me know if you can help.AttachmentET200SP and CM Ptp.pdf (178 Downloads) |
5/22/2025 6:37 AM | |
Joined: 4/28/2015 Last visit: 9/10/2025 Posts: 113 Rating:
|
i'm not totally sure but it looks like you are trying to read modbus registers from “extended range” (4xxxxx instead of 4xxxx). Seems you probably need some prerequisites for that, see here Normal modbus rtu works for me once i change a parameter as shown here: |
Last edited by: Moderator_Lan at: 05/22/2025 07:09:49Link opzimized/ Image embedded from Link |
|
This contribution was helpful to
1 thankful Users |
5/25/2025 9:26 AM | |
Joined: 4/27/2025 Last visit: 8/14/2025 Posts: 4 Rating:
|
It's working now. I only inserted the communication module with the CPU. I'm not sure if it needs a specific location or if it was incorrectly placed in the rack. |