11/25/2024 10:53 PM | |
Joined: 4/28/2015 Last visit: 8/31/2025 Posts: 7 Rating:
|
Similar issue. I had just loaded up the second identical machine we are building and had all network and hardware configs loaded, everything working but just no communication between PLC and HMI. Also grey topology lines between PLC and HMI. set the correct date and time on the HMI and communication works straight away. Line is still grey though... ------------------------------------------------------------------------------------------ |
Last edited by: Moderator_Lan at: 11/26/2024 07:44:25New subject after splitting |
|
11/29/2024 10:09 AM | |
Joined: 8/3/2009 Last visit: 9/16/2025 Posts: 16436 Rating:
|
Hello ShannonG Often if you have this issue with date/time and teh HMI communication there are also systemalarms on the HMI that indicates this: https://support.industry.siemens.com/cs/de/en/view/109800515 Bye Murof |
If this Information really helps, you could use the Rate function |
|