8/3/2023 4:14 PM | |
Joined: 2/17/2020 Last visit: 8/29/2025 Posts: 1251 Rating:
|
Hi, I believe that through DP you could only access the Comfort Panel keys. For this application, as Murof has commented, communicating via OPC UA would be recommended. There is even the application example attached: Communication Between a Beckhoff PLC and a Comfort Panel via OPC UA |
A rating will be well appreciated. |
|