10/14/2010 2:40 PM | |
Posts: 24 Rating:
|
the next picture of Interface module |
Last edited by: Eng.Mohamed at: 10/14/2010 2:41 PM |
|
10/14/2010 2:42 PM | |
Posts: 24 Rating:
|
The picture of PLC |
10/14/2010 3:27 PM | |
Joined: 9/27/2006 Last visit: 9/3/2025 Posts: 12397 Rating:
|
Hello Mohamed; From your 3rd photo, it looks like you have a 545-1101, or close, WinCC Flexilble has integrated nterfaces for the 505 CPUs: WinCC Flexible 2008 Communications, Part 1:http://support.automation.siemens.com/WW/view/en/187975528.1.1 Communication partner (SIMATIC 500/505)IntroductionThis section describes communication between HMI device and SIMATIC 500/505 controllers.With SIMATIC 500/505, the connections use protocols that are specific to the PLCs: ● NITP Serial connection over the RS-232/RS-422 interface with the NITP protocol (Non-intelligent terminal protocol) ● PROFIBUS DP PROFIBUS DP is master-slave fieldbus with up to 122 slaves. Normally, a PROFIBUS DP network is operated by one master. This master polls all slaves cyclically. The master could, for example, be a PLC with interface module that is compatible with the DP standard. Each HMI device is a slave and is assigned permanently to a master. Your CPU does not appear to have a Profibus-DP port, so you will be using the serial NITP protocol for your exchanges. Just follow the procedures suggested in the WinCC Flexible manual to install the driver and configure the comm links. You will have to rebuild the application for the operator panel, of course, but I think you already understand that. You should look at the 505 system manual for details on communication hardware on the PLC: http://support.automation.siemens.com/WW/view/en/17514935 See chapter 3 for the dipswitch setup and pinout description of the PLC's communication ports, RS-232 and RS-422 Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 10/14/2010 3:28 PM |
|
Follow us on