Suggest Don't worry about UPS. you should make preparation for data lose #1--Back up all NC/PLC data to HMI or transfer to external PC save on HDD #2--810D has battery on the board which will be back up RAM data during power off. finally if the 810D board (with good battery ) cannot hold data during power off (power failure) you need fix it or replace with an good one. if you really want to UPS power , just add one Monitor Module , which supply low control voltage to CCU. supply monitor Module with UPS power (3 phase AC 308V) Monitoring module 6SN1112–1AC01–0AA1--check document with my attached file. AttachmentPJU_0613_en.pdf (176 Downloads) |