4/15/2008 8:11 AM | |
Joined: 9/27/2006 Last visit: 9/11/2025 Posts: 12407 Rating:
|
Hello jopsgar; First, the CPU224X has 2 ports, you can set Port0 to communicate with MicroWin, and Port1 to connect to the Panel. if you use no extenal comm ports on the PLC. For communication options, you can use PPI or MPI networks if you use the integrated ports, Profibus or Ethernet with add-on comm processors, look at the following manual, chapter 2: http://support.automation.siemens.com/WW/view/en/18797552 Once you have the comms setup, you will need to configure screens and tags in WinCC flexible for basic exchanges between the panel and the PLC; you might need Area Pointers if you need to implement some more delicate functions, like alarms and alarm acknowledgement. The manual I mentionned touches on these , and the following gives you a great basic presentation of the functionnalities for a panel program.(WinCC flexible 2005 Getting Started): http://support.automation.siemens.com/WW/view/en/18660846 Once you have looked at these, come back with specific questions, we may be able to help you more. Hope this helps, Daniel Chartier |
4/15/2008 9:50 AM | |
Joined: 4/24/2006 Last visit: 7/31/2025 Posts: 9027 Rating:
|
Hi JOSGAR, Perhaps the following link might help: http://support.automation.siemens.com/WW/view/en/19323674 Best regards, Wizard |