Hi experts, There is a PCS7 upgrade (v8 to v10) that will also upgrade the ET200M to ET200SP (not HA). I saw this document for upgrade of ET200M to ET200SP HA, which seems to recommend the use of another software called Process Automation Accelerator (PAA): Upgrade ET 200M to ET 200SP HA The document seems to suggest that the upgrade of ET200M to ET200SP HA will also necessitate some program adjustments (IO address? Channel drivers replacement?), and PAA will help on this. My question is would this also apply in ET200SP (not HA)? What exactly will be the program adjustments, am I right the IO address will move and will need new channel drivers? Are there more? We should be able to do these program adjustments without PAA right? Thanks you so much for any response. |
Last edited by: G_R_E_Y_31 at: 04/08/2025 03:49:46Last edited by: Moderator_Lan at: 04/08/2025 07:44:36link optimized |
|
4/9/2025 9:07 AM | |
Joined: 1/11/2019 Last visit: 8/14/2025 Posts: 899 Rating:
|
1. Do the program adjustments apply for ET200SP (non-HA)? Yes, some program adjustments are needed even when migrating from ET 200M to ET 200SP (non-HA), although less complex than for HA systems. Here's why:
Because of these differences, the program and hardware configuration in the PCS 7 project will not be a direct drop-in replacement. 2. What program adjustments are typically needed? Here's what typically needs to be updated: a. IO Addresses Change
b. Channel Driver Adjustments
c. HW Config / Topology Adjustments
d. Symbolic addressing may need updates
3. Do we need Process Automation Accelerator (PAA)? PAA is a productivity tool introduced by Siemens to help automate the migration of IO configurations and logic blocks, especially useful for large or complex HA projects. But for your case:
So yes, you can do these adjustments without PAA, especially in smaller systems. Recommended Approach Without PAA
|