11/9/2018 10:51 AM | |
Joined: 1/22/2018 Last visit: 11/11/2024 Posts: 31 Rating: (0) |
I have a problem with my MM440 running remotely. I use terminal 5 (DIN 1) for starting the motor, P701 = 1 (ON/OFF), all other paramers for DI are 0 - disabled (P702 - P708). P700 = 2 P1000 = 2 Frequency is controlled by the AI1 (0 - 10 V), and that is working fine. The DIN 1 is connected correctly and it is getting input (+24 VDC) on terminal 5 when the START is given. But the MM40 doesnt start the motor (like there is no command for the START or the remote control isnt activated - but i put parameter P700 to 2 - terminal comand source ). I tried changing the DI at terminal 6, but it was the same. Could someone give me advice what to do next? BR THOMPSONvk ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 11/12/2018 9:44:32 AMNew subject after splitting |
|
11/12/2018 6:54 PM | |
Joined: 6/4/2008 Last visit: 11/12/2024 Posts: 1505 Rating: (326)
|
Hi, you need to ensure that each enable (bit 1 to bit 6) as per page 286 of the manual linked HERE are set to Logic '1' (or enabled by some other means). Your Digital input already setup should then start the drive by toggling ON/OFF1 Regards, Graeme |
Last edited by: Jen_Moderator at: 11/13/2018 10:24:30 AMOptimized link. |
|
This contribution was helpful to1 thankful Users |