We are having PCS 7 with 410-5H controller Suddenly it is going to stop mode Then we power off\on as we do normally and then STOP Led blinking , i thought it was rebooting it will take some , after waiting 25 mins it was same, then i try to connect from ES and tried downloading back up, But is is showing error related to 0 POs availble at CPU, then i understood, it is related to SE card problem, removed and putback SE card 3 to 4 times, At 4th time it was solved, this problem was repeated twice 6 months. Is any facing same issues with 410-5H Do weneed to upgrade any firmware Is problem is coming due to Power supply Plz anyone support , ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 05/24/2019 10:48:03New subject after splitting |
|
5/23/2019 3:31 PM | |
Joined: 9/9/2015 Last visit: 10/28/2024 Posts: 728 Rating: (280) |
Hello, Next time if the CPU stop suddenly without any reason, you can go to module information of the PLC (Ctrl+D), then go to "Stacks" , you will see somethings there. Only when PLC stopped. |
Please give me 5 stars Rating if my post is helpful for you. :) |
|