7/1/2013 11:07 AM | |
Posts: 43 Rating: (9) |
Dear Expert, Please suggest me for selection of Isolator, Contactor & O/L relay for 22KW Motor with 380V, 60HZ system.
|
7/1/2013 11:27 AM | |
Joined: 5/28/2008 Last visit: 5/11/2024 Posts: 4506 Rating: (836) |
Hello, Useonline configratorsfor selection of most suitable products for your application
|
Ayman Elotaify |
|
This contribution was helpful to2 thankful Users |
7/1/2013 11:40 AM | |
Posts: 43 Rating: (9) |
Thanks, but how to start & select the isolator, pls suggest me.
|
7/3/2013 8:40 AM | |
Posts: 43 Rating: (9) |
Sorry, but i just want type-2 selection chart for 380V, 60Hz, 22KW motor. |
7/3/2013 9:18 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (872) |
Please see the attached file. Mayhelp you.
Attachment22Kw motor type 2 co-ordination selection.pdf (311 Downloads) |
This contribution was helpful to1 thankful Users |
7/3/2013 1:56 PM | |
Joined: 2/12/2013 Last visit: 12/6/2023 Posts: 61 Rating: (15) |
I think this is for 415V AC Supply, not for 380V AC.
|
7/4/2013 6:01 AM | |
Posts: 47 Rating: (8) |
Hi, if you will go to the online config. for motor feeder selection, it neither gives u option of 380Volts nor it will give you on 60Hz. I have calucalted the sizing of motor feeders as under:- 1) Motor Rating: 22KW 2) Voltage: 380V; Ferquency: 60Hz 3) Full load current: 46A 4) Inrush Current for DOL: 331.2A ( approx @ 7.2 times of rated current) ---------------------------------------------------------------- Contactor: 3RT1044 MPCB: 3RV13 41-4HC10 Relay: 3RU11 46-4HB0. This is as per TYPE 2 Co-ordination. Hope this will solve your problem |
Follow us on