3/20/2007 10:27 AM | |
Posts: 26 Rating:
|
Hello, I still have the same problem when i try this. In attachment you can see our project. I hope you can help me using this.. Thanks in advance, JAsVAp AttachmentActive_2.zip (1021 Downloads) |
3/20/2007 11:06 AM | |
Joined: 10/11/2006 Last visit: 9/15/2025 Posts: 6020 Rating:
|
Hello, I checked your project (only due to your start up problem) and found some wrong parametersettings. I corrected in Vector: p860 from 0 to VECTOR_03.r863.1; p864 from 1 to A_INF_02.r863.0; in ALM I changed: p840 from 1 to VECTOR_03.r863.1. Switching ON with a fixed 1 is not possible, so if there is only one axis like inyour case, the r863.1 from the axis is the easiest way to control the ALM. Attached find the project with the changes. Best regards TechTeam AttachmentActive_2_changed.zip (991 Downloads) |
With best regards, |
|
3/20/2007 12:10 PM | |
Posts: 26 Rating:
|
Hi, thanks for it but i have another problem now. When i press the green button i get error 7802 after some seconds. I guess every enables of ALM and Motormodule are OK, so i guess ready for operation. Maybe there is something wrong with the line contactor feedback? or something else.. I attached again our project, thx JAsVAp AttachmentForumbac.zip (864 Downloads) |
3/20/2007 2:23 PM | |
Joined: 10/11/2006 Last visit: 9/15/2025 Posts: 6020 Rating:
|
Hello, AttachmentSeiten aus SINAMICS_S120_Commissioning_Manual_0306_eng.pdf (1184 Downloads) |