4/20/2017 8:02 PM | |
Joined: 2/3/2011 Last visit: 5/29/2024 Posts: 346 Rating: (10) |
Hi, For the same situation, can S7-1500 be used in Multiprocessor Mode? ------------------------------------------------------------------------------------------ |
Last edited by: Min_Moderator at: 4/21/2017 9:40:10 AMNew subject after splitting |
|
4/20/2017 8:46 PM | |
Joined: 9/27/2006 Last visit: 6/5/2024 Posts: 12260 Rating: (2670) |
Hello syd; The largest, most powerful CPU928 (the CPU 928B) had 64 kB of work memory, non-expandble, for code and data. This is why Siemens proposed ways of coordinating more than one CPU to control a large process (the coordination module 923c). The smallest CPU of the S7-1500 family (the S7-1510) has more program memory (for code) than 2 CPU 928B, see the screencapture below taken from the sSemens Industry Mall: https://mall.industry.siemens.com/mall/en/WW/Catalog/Products/10204208?tree=CatalogTree If you decide to replace your S5 controller setup with any of the current S7-1500 CPUs you should not need to use multicomputing (multiple controllers sharing the load of a project on a single rack). You should be able to reprogram the project in a single processor. In any case, s7-1500 does not have the multicomputing option. The only S7 family that does is the S7-400: What is multicomputing mode and what are the differences to operating in the segmented subrack? Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 4/20/2017 8:49:34 PMLast edited by: dchartier at: 4/24/2017 8:43:58 PM |
|
This contribution was helpful to1 thankful Users |
Follow us on