2/10/2020 2:48 PM | |
Posts: 9 Rating:
|
Thank you for the welcome! As you figured out, I am VERY new to this so please bare with me here. I figured somethings out but my solution is not very elegant. For example the temperature at start up should be around room temperature but what if it is not and it is lower than BOO2 (cool) ON threshold? Then the system begins with heating instead of cooling and that is not what I want. Any insights? Thank you very much! Attachmentcool_heat_test_v2.zip (464 Downloads) |
2/10/2020 2:57 PM | |
Joined: 12/18/2014 Last visit: 9/13/2025 Posts: 35957 Rating:
|
Which temperature should serve as the setpoint? 20 ° C? 22 ° C? Do you want to keep this variable? |
2/10/2020 3:38 PM | |
Posts: 9 Rating:
|
Well, I came up with this, which does start with cooling even if the temperature at start up is between 0C and 10C. It works but it is not very pretty Attachmentcool_heat_v3.zip (463 Downloads) |
2/10/2020 3:39 PM | |
Joined: 12/18/2014 Last visit: 9/13/2025 Posts: 35957 Rating:
|
I hope, I understand you right. The setpoints can be changed via Display. Attachmentcool_heat_test_v3.zip (502 Downloads) |
Follow us on