Hello, This fault message class is related with power supply. So please check your input supply voltage for any fluctuation/spike/dip etc. etc. How many times this fault is triggered? How is input supply bus? |
9/24/2022 9:28 AM | |
Joined: 2/22/2017 Last visit: 7/6/2024 Posts: 2 Rating: (0) |
hello , this fault occurred after around two hours of production and it persists , we toggle it to alarm in order to not stop production after that the problem seem fixed , but we scared if this fault can cause any damage to driver . what do you mean input supply bus? thanks for your support . best regards. |
Last edited by: ramdhane at: 09/24/2022 09:30:14Last edited by: ramdhane at: 09/24/2022 09:31:51Last edited by: ramdhane at: 09/24/2022 09:33:48 |
|
9/24/2022 10:20 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (877) |
Input supply transformer (if any), input supply cable size, other connected electrical load on same power distribution panel etc. etc. |