Hi, Of course it's possible to start, hold, complete, abort, resume etc. the SFC by connecting the signals via a button. Make sure that input PARAM is set to 1 for one cycle before starting the SFC. This will make sure the Control Strategy and Setpoints are validated. Without this setting to 1, the SFC won't start. Also, make sure the Setpoints are set within the low and high limit range. The PARAM will also validate the setpoints. If they are not valid, the SFC won't start also. |