1/12/2020 7:13 PM | |
Joined: 2/1/2016 Last visit: 5/13/2024 Posts: 2 Rating: (0) |
Dear all, Need your help! I have configuration in Step7 5.6 HF3, with F-CPU ET200S-CPU: 6ES7151-8FB01-0AB0, and RIO modul ET200SP: 6ES7155-6AU01-0CN0. On RIO modul I have configured couple standard DI, DO, AI and one F-DI (6ES7136-6BA00-0CA0) and one F-DO (6ES7136-6DC00-0CA0). I made settings for F Parameters of the F-CPU (you can see attached picture) - Base for PROFISafe Address : 2000. Also, made settings for Parameters of the F-DI/F-DO, regarding to wiring. In Simatic Manager in Edit Safety program, create F-Runtime Group, compile and download to F-CPU (program consistent). I get faulty F-DI and F-DO modules with diagnostics: F_Source_Add and Parameters are wrong (there is a print screen) and also SF on F-CPU. DIAG LED on module flashing red, and Channel Status led are steady Red! What could be wrong!? AttachmentSafety_support.zip (152 Downloads) |
1/12/2020 7:41 PM | |
Joined: 5/6/2010 Last visit: 5/19/2024 Posts: 1965 Rating: (274) |
Hello, do you assign the F-addresses to the ET200SP-modules? regards |
2/11/2021 11:38 AM | |
Joined: 4/6/2018 Last visit: 3/16/2022 Posts: 1 Rating: (0) |
Hello I have the same problem. Did you solved it? Thanks |
2/12/2021 1:53 PM | |
Joined: 3/11/2019 Last visit: 5/23/2024 Posts: 1433 Rating: (261) |
Dear all, i assume the ET200SP was configured via GSD. If yes, you will need the S7-FCT to assign the safety parameters. After installation you find per right click on the module the menu "Device-Tool". S7-Fail-safe Configuration Tool (S7-FCT)maybe this helps |
Last edited by: sancruz at: 02/12/2021 13:59:22Feedback appreciated, please rate |
|