Hello, Is it possible to connect a Field-PG to a PLC S5-150U? B.r. S-O J |
9/20/2005 11:37 AM | |
Joined: 8/10/2005 Last visit: 4/9/2024 Posts: 1486 Rating: (32)
|
if there is a AS511-Interface in the PLC S5-150, then it is possible to go online with Field PG and any STEP 5 V7.x To connect the Field PG to the AS511-Interface you need a special cable. Such a cable can´t be ordered, you have to create/build it by your own. The Pinout of that cable is avilible at following URL: http://support.automation.siemens.com/WW/view/en/217845 Best regards Christian Kessler Technical Support for Automation & Drives |