Hello, To use the PID to control this set-up , you can try FB41 that is applicable for most of the processes in industry.To have a good initial view, read the online manual and then check the following sample:
hd_FB41_EX.zip and these clustered threads: HD_PID Control Package - FB41 Samples For you application,as you processed the process value before PID block put PVPER_ON=False and put your process value in PV_IN.The suitable output of algorithm will be available in LMN output if you select the proper switches and PID parameters. I hope this helps, Hamid Hosseini |
Last edited by: hdhosseini at: 10/22/2014 2:03 PMLast edited by: hdhosseini at: 10/22/2014 1:55 PM |
|
This contribution was helpful to1 thankful Users |