Hello, personal e-mail IDs are not allowed in this forum. You can write here your problem so that other forum members can also help you or you can send me personal message fpr any specific query/doubt. BTW to enable infeed module, ON/OFF1 must be on i.e. it positive edge detection & OFF2 must be 1. Please check in your case why OFF2 is 0. You need to check your PLC program. You can check it on line. |