2/27/2019 7:50 AM | |
Joined: 10/17/2007 Last visit: 6/6/2024 Posts: 4002 Rating: (347)
|
I attached detail in the file please follow the steps and post here feedback BTW: if your control display in German, try to set NCMD250=1 , it may turn to your language Attachment810_820 reload.pdf (505 Downloads) |
Last edited by: nulizhang at: 2/27/2019 7:53:29 AMIf you like my comments please |
|
This contribution was helpful to1 thankful Users |
2/28/2019 12:25 PM | |||||
Posts: 6 Rating: (0) |
I followed the procedure completely but the PLC STOP still stands. The following alarm still appears:
Any ideas on how can this be solved? Also how can I connect my normal pc with a DB9 9-pin serial port, to the front interface of the Sinumerik in order to communicate directly with the PLC through S5W (Step 5 for Windows)? I see in page 6-19 of the document 810_GA2_Installation_Instructions.pdf a cable layout but this was used for the PG 6xx series of field programmers, which I do not have. I believe there must be a way to connect and send the S5W project file directly to the PLC, am I wrong? Thank you very much. |
||||
3/1/2019 6:54 AM | |||||||||
Joined: 10/17/2007 Last visit: 6/6/2024 Posts: 4002 Rating: (347)
|
Key point for you how to connect PLC in 810T to PG (S5): --you need the same cable same as you transfer NC MD (%TEA1) --You must connect to front panel D type 25 pin interface ---Going to SETTING DATA --SETTING BITS--set 5010=0000 0100 ---Going to DATA IN/OUT--DATA IN --START ----Going to your PG with S5 making PLC on line (some time F3 sone time mouse click )
|
||||||||
If you like my comments please |
|||||||||
This contribution was helpful to1 thankful Users |
3/6/2019 1:12 PM | |
Posts: 6 Rating: (0) |
Well, I managed to connect to the PLC, now the machine has all the supposedly correct data. I have uploaded: TEA1 TEA2 All the other data. I managed to connect directly to the PLC using Step 5 for windows and sent the program to the PLC. The machine starts with no errors, but I have a major problem. The PLC does not seem to be acting on the various outputs. I checked on the Diagnosis and the Inputs are updating. I checked also through Step 5 if there was any error in the PLC and it does not give an error. Is there any PLC-MD special procedure that has to be performed in order to put the plc working? I also checked the red led on the CPU card and it starts lit up and after a while it turns off, meaning, according to the manual, that everything is running OK. What can the problem be? Does anyone have any idea? Thank you in advance. |
3/7/2019 6:24 AM | |
Joined: 10/17/2007 Last visit: 6/6/2024 Posts: 4002 Rating: (347)
|
I am happy to hear you connected PC (S5) to 810T, if you connected with my help can you please rate my answer , such as some Thanks button at the bottom. Then for you this post --Can you make sure "YOUR 810T PLC CPU is RUNNING" that very easy --ther is no PLC STOP alarm on screen --means PLC running
|
If you like my comments please |
|
This contribution was helpful to1 thankful Users |
3/7/2019 11:47 AM | |
Posts: 6 Rating: (0) |
The PLC is running, the is no PLC Stop alarm and also the process of startup is correctly performed, namely, the red led on the back of the CPU card lights up when restarting and after starting up, it turns off, which, according to the manuals, means the PLC is correctly started. There is no action on any part of the machine, which leads me to believe that the PLC is not performing any of its functions. I can post the PLC project for Step 5 here if it helps. I do not know a lot about this PLC language, but to my understanding and from what I read in the PLC Programming manual, the basis seems to be functional. Maybe I am missing something. Thank you for your help. AttachmentPLCS5.zip (340 Downloads) |
3/7/2019 12:22 PM | |
Joined: 10/17/2007 Last visit: 6/6/2024 Posts: 4002 Rating: (347)
|
Thanks for your feedback. But I cannot help you by reading PLC program, actually No one can help like that. What you need to do is finding out original PLC program Backup--PCP and original PLC MD --TEA2 |
If you like my comments please |
|