ok perfect, one thing more; in myPID increasing PV should decreasing the OUT,which is the parameter to dothat ? Splitted from about PID with FB41. |
Last edited by: O_Moderator at: 6/10/2011 12:35 PMnew subject after splitting |
|
6/10/2011 12:19 AM | |
Joined: 1/28/2009 Last visit: 8/31/2025 Posts: 6874 Rating:
|
You can select the type of action: 1- direct action (SP>PV), so initialy, increasing PV decrease the error and also decrease the LMN (value on actuator) 2- reverse action (PV>SP),so initialy, decreasing PV decrease the error and also decrease the LMN (value on actuator)-->(negative P) Also check this topic: Determine reverse or direct action of PIDregards |
Last edited by: hdhosseini at: 6/10/2011 12:20 AM |
|
This contribution was helpful to
1 thankful Users |
6/10/2011 4:48 AM | |
Joined: 5/28/2008 Last visit: 9/3/2025 Posts: 4522 Rating:
|
Hello, For tuning PID loop, please read carefully the answers of Pegaia on this thread. Hope it helps.
|
Ayman Elotaify |
|
6/10/2011 9:21 PM | |
Joined: 1/28/2009 Last visit: 8/31/2025 Posts: 6874 Rating:
|
Also check the following links, I think they would be really helpful: PID Self Tuner: Example Adapted to Standard PID Control V5.1 PID Self-Tuner V5 regards |