Hi Everyone, When we are attempting to initiate the IO test for the CPU 1214C DC/DC/DC with the IM155-6 PN HF (High Feature) IM Module, the IO modules within the IM are consistently unresponsive, displaying a value of 0. Despite all system indicators in the modules showing green without any error messages, there are no flashing green lights indicating activity. Any idea what would be the issue and could be compatibility issue if so, why it is not showing in the TIA portal software? Expecting any quick response. Thank you so much your response. With regards Arun ------------------------------------------------------------------------------------------ |
Last edited by: Wit_Moderator at: 09/13/2024 11:57:10New subject after splitting |
|
9/15/2024 12:47 PM | |
Joined: 5/22/2024 Last visit: 9/18/2024 Posts: 2 Rating: (0) |
Hi, We have identified the issue based on the error message on IM module which is lower-level compartment but unfortunately, we couldn't download the 4.2.3 firmware update from siemens portal. Kindly anybody help us. Firmware Update for ET 200SP IM 155-6 PN HF - ID: 85624387 - Industry Support Siemens |
9/17/2024 12:04 PM | |
Joined: 9/21/2012 Last visit: 11/19/2024 Posts: 4199 Rating: (474) |
The link works fine, you can download the firmware files from there. Download the latest, v4.2.4. If you have not registeder you forum user for download rights, it takes a few working days for Siemens to activate the download rights, if the export restriction are ok. |