9/2/2021 12:42 PM | |
Joined: 3/5/2014 Last visit: 8/5/2022 Posts: 5521 Rating: (1054)
|
hi remeeus, I am sure ther is a response. have a look to this: How do you evaluate the status of system blocks in STEP 7 (TIA Portal)?Status is just valid for one cycle. you can´t see it with bare eyes. hope this helps, regards, |
FCK WAR! |
|
9/2/2021 1:35 PM | |
Joined: 5/16/2018 Last visit: 2/12/2024 Posts: 5 Rating: (0) |
Why didn't i think of that.......Thank you very much! Okay, now we do have a response..... 80C8 witch indicates a slave timeout, (Check the baud rate, parity and the connectors on the slave.) And again with the ICHAR_GAP value of 1 it doesn't generate the error. It does interpret the answer only it takes about 8 seconds Witch is odd because im am monitoring the communication with a scopemeter and my Moxa uport with a serial port analyzer. They both indicate a interpretable answer in time frame of about 120ms
|