Industry Online Support
Technical Forum
7/20/2009 8:55 AM | |
Posts: 3093 Rating:
|
Hello Richard, do you get the ERROR-Bit and an error number in STATUS at FB Modbus? Regards, Kaulquappe |
7/20/2009 8:02 PM | |
Joined: 12/22/2006 Last visit: 1/25/2022 Posts: 1742 Rating:
|
hello, From all previous messages, i come to the conclusion that the problem is not at the Siemens PLC side, but more at the Schneider side. In my opinion, the following is happening: - after a connection loss (for instance after power down of the Siemens PLC), the PLC sends a SYNC message to the Schneider system (this is the requestfor a new connection) - but the schneider CPU considers that the prevouis connection is still active and does not accept the new connect request. - untill the connection keep alive timeoutis reached at the Scnieder side. To be very sure of that, you could take a trace of the traffic on the wire by using "wireshark" on a PC used as monitoring system + a hub (or a switch with port monitoring capability like scalance X200). Wireshark is a freware (see www.wireshark.org) Look if you can reduce that timeout at the schneider side to accelerate the acception of a new connection. |
Best regards |
|
Follow us on