1/20/2017 7:22 AM | |
Joined: 3/14/2008 Last visit: 11/14/2024 Posts: 2130 Rating: (953)
|
Goodmorning nicopoi, You are on the right track! In order to open the OS project on the "remote ES", you have to do the following: - Activate OS multi user engineering for the multiproject (which you already did) - Open Simatic Manager on the remote ES and click on File->Open and navigate to the main ES (where the project is located). Now you have connected the remote ES and thus you can open the OS project. If you need additional info about this topic, check out the following link: |
Last edited by: Oreca at: 1/20/2017 7:23:57 AMIf I could help you, you can use the RATE button. Thank you. |
|
1/20/2017 11:24 AM | |
Joined: 3/14/2008 Last visit: 11/14/2024 Posts: 2130 Rating: (953)
|
Hi, You have installed the same PCS7 version, but does it have the same options as well (Add-ons, updates, hotfixes etc.)? Please bear mark the following (copied from manual): The project path under "Storage location for projects/multiprojects" is set by default to "SIEMENS\STEP7\S7Proj" and all necessary access rights are set for this project path. If you use a different project path, you need to set the necessary access rights with the tool "SimaticRights.exe". To do this, start open the SIMATIC PCS 7 DVD 2/2 and run the program "SimaticRights.exe" located in the folder "Additional_Products\SimaticRights" by selecting "RUN as Administrator". Enter the new project path in the dialog or select it. The new project path must be available when the tools are started. |
If I could help you, you can use the RATE button. Thank you. |
|
1/23/2017 8:14 AM | |
Posts: 567 Rating: (107) |
Hi Nicopoi, configure the network adapter for the terminal bus in the SIMATIC Shell on the ES client and it should solve the issue. |
1/25/2017 3:48 PM | |
Posts: 567 Rating: (107) |
Hi nicopoi, did you solve the Problem? If yes how could you solve it? Thank for answer! |