Hello, the automatic setting of the input scaling requires the information to which hardware input the Input_PER parameter is connected. This information is only available for the PID call, so the automatic setting can only be used in the "Properties" tab of the inspector window of the programming editor. Select the PID call in the programming editor and open the "Properties" tab, see attached screenshot. The technology object configuration editor in the project navigation only handles the data of the PID instance DB. The instance DB does not have the information to which hardware input INPUT_PER is connected or even if the PID is called at all. Because of this the "Automatic setting" is disabled in the technology object configuration editor. A description is also available in PID online help Regards |
7/2/2024 4:16 AM | |
Joined: 12/13/2023 Last visit: 10/11/2024 Posts: 2 Rating: (0) |
Thank You! This was the solution. |