1/28/2011 8:38 AM | |
Joined: 3/21/2006 Last visit: 10/7/2024 Posts: 10229 Rating: (1181)
|
Both numbers are not valid like Siemens product numbers. You need 6SE7090-0XX84-6FF5 The other point is - yes, you can use profibus address to connect to master but you need also to set another parameters in drive in order to control it via profibus. Best regards, Hristo Mihalev |
1/28/2011 1:28 PM | |
Posts: 12 Rating: (0) |
Thnaks for the quick response. it was helpful. will try it out on monday. |
2/2/2011 4:17 PM | |
Joined: 3/21/2006 Last visit: 10/7/2024 Posts: 10229 Rating: (1181)
|
So, let's separate the issues. One side is "How to make parametrization in compact logix side?" - I don't know. At least you need correct GSD file corresponding to the Profibus card. And then in software you should assign how many words will be exchange. Look at http://support.automation.siemens.com/WW/view/en/20386822 There you'll find simple project how to exchange data (control the drive and receive statuses from it) with master CPU.(unfortunately this is a Siemens PLC). The other side is "How to make parametrization in to drive?". For this you need DriveMonitor 5.4.2.0 plus connection cable. All info is available at SIMOVERT MASTERDRIVES Vector Control Compendium VC34 (Operating Instructions) . I am afraid only using drive panel for you will be a little bit difficult to "adjust" all necessaries drive's parameters. Best regards, Hristo Mihalev |
2/3/2011 8:39 AM | |
Posts: 12 Rating: (0) |
Where can i find the correct GSD file for 6SE7037-0E.... for the one i have for using with prosoft profibus scanner PS69-DPM, it shows up as Siemens AG ASI1 i downloaded it from the siemens website. is that the correct one? i have also attached the screens for the prosoft configurator using the GSD file i have. Which module should be selected in the first screen? I will be happy to give you a call if u are available. Attachmentprosoft-settings.pdf (938 Downloads) |
2/3/2011 9:44 AM | |
Joined: 3/21/2006 Last visit: 10/7/2024 Posts: 10229 Rating: (1181)
|
You need a GSD file for Profibus card. Not for the drive. Look at http://support.automation.siemens.com/WW/view/en/48172137 So, your GSD file is for the Station type: MASTERDRIVES / DC Master CBPx Order no.: 6SE7090-0xx84-0FF0/0FF5 Version: 10/2000. (old one). If the card is newer you should use Station type: MASTERDRIVES/DC MASTER CBP2 DPV1 Order no.: 6SE7090-0xx84-0FF5 Version: 07/2004. Then you should select from availble modules and configured. These steps concerning only PLC hardware side. To be possible to control the drive into software you should send and receive from drive data. Really remotely isn't possible to help you more. You need at least Siemens driver specialist to commissioning the drive, if we assume all necessaries steps in PLC side will be finish by you. Did you try to find in Google some example project contents siemens drive plus your type of CPU? Best regards, Hristo Mihalev |