S7-200 CPU224 with EM277 8sets can link via profibus to KTP600 Basic as master Tanapol Logix |
7/13/2010 7:49 PM | |
Joined: 9/27/2006 Last visit: 5/5/2024 Posts: 12257 Rating: (2666) |
Hello Tanapol; The following FAQ lists the different panels, including the KTP600, and shows the maximum number of simultaneous connections available for each. http://support.automation.siemens.com/WW/view/en/15363798 It states that the KTP600 can only open 4 connections simultaneously. To read continuously from 8 CPUs you would need 8 connections. The same FAQ proposes an alternative, "switched connections", where the CPUs are not connected all at the same time, but selected by WinCC Flexible programming. See if it can help you out. Hope this helps, Daniel Chartier |