6/1/2012 9:47 AM | |
Joined: 9/6/2008 Last visit: 5/7/2022 Posts: 1121 Rating:
|
Hi well if you say full redudant do you want IO redudancy. If in case no the IO quantity will not double as in case of IO redudancy For the Hardware, you will need, 1. UR 2H rack (9 Slot) - 2 Nos. 2. PS 407, 10 A - 4 Nos 3. CPU 417 - 2 Nos 4. CP443-1 - 4 Nos 5. Sink Module - 4 Nos 6. FOC cable - 2 Nos 7. FEPROM 16 MB - 2 Nos For IO quantity Please find the attached Excel sheet for calculating the IO quantity and the Racks. You will have to fill the No of IO, Spare and the Excel sheet takes care of the rest. Have fun.... AttachmentIO list Template.zip (89 Downloads) |
Jazz |
|
6/1/2012 1:19 PM | |
Joined: 9/27/2006 Last visit: 8/7/2024 Posts: 12273 Rating:
|
Hello mohalomari; To add to Tagolover's information, download and studythe manual for the S7-400H system, you will find theremany descriptions for different configurations of fault-tolerant systems: SIMATIC Fault-tolerant systems S7-400H You will find an extract from the manual showing the different hardware required to create a H-system as an attachment. Hope this helps, Daniel Chartier |