Hi, You need the library "USS and Modbus" to do anything with Modbus on the freeport of the S7-200. But a S7-200 can't be a master.. See also the handbook : S7-200 System Manualon chapter 12 is everything what you need for the Modbus Slave. STEP 7--Micro/WIN Instruction Libraries makes communicating to Modbus master devices easier by including pre-configured subroutines and interrupt routines that are specifically designed for Modbus communications. With the Modbus Slave Protocol Instructions, you can configure the S7-200 to act as a Modbus RTU slave device and communicate toModbus master devices. |
I hope that the answer will help, if you have still questions, don't hesitate to ask me. |
|
2/18/2007 6:13 PM | |
Posts: 2 Rating: (1) |
Yes it is possible use S7 200 How master modbus. There is a library that you make this.
Attachmentmodbus.zip (534 Downloads) |
This contribution was helpful to1 thankful Users |
7/30/2007 7:26 PM | |
Posts: 22 Rating: (1) |
Dear Sir, Find attached the manual for the MODBUS Master Library. Regards Attachmentmodbus_master_lib_S7-200_en.pdf (550 Downloads) |
This contribution was helpful to1 thankful Users |
7/30/2007 7:30 PM | |
Posts: 22 Rating: (1) |
Dear Sir, I forgot to mention that in the posted manul there was an example. Regards |