12/8/2019 4:10 PM | |
Joined: 9/27/2006 Last visit: 11/18/2024 Posts: 12296 Rating: (2691)
|
Hello mansourkh; What exactly do you mean when you say the S7-400H "releases" its fiber-optic connections? The fiber-optic links between the CPUs can become faulty, and need to be replaced, or one of the CPUs can become damaged or present a fault that shuts it down. These cases are shown in the following diagrams, taken from the S7-400H manual. SIMATIC Fault-tolerant systems S7-400H (V6.0) https://support.industry.siemens.com/cs/us/en/view/82478488 In such a case there will be active LEDs on the CPUs, either Redundancy (for the fiber-optic link ;loss) of Busfx or SF for the faulty CPU. You should always start by opening the diagnostic buffer of the faulty CPU to see what messages are logged; this generally will also give you a description of the probable cause of your problem. Read the manual (section 11.3 mainly) to see how to diagnose the problem. In a Y-link, the IM 153-2 redundant interface modules will hold the diagnostics for the underlying Profibus slaves. See our friend fritz's reply to this thread for suggestions on how to read the diagnostics from the Y-Link. Giagnostic for Y-link and DP-slaves after him Hope this helps, Daniel Chartier |
12/9/2019 11:43 AM | |
Posts: 12 Rating: (0) |
system is running now,but We checked this state for critical situations and find that. |
12/9/2019 1:43 PM | |
Joined: 12/12/2018 Last visit: 7/1/2020 Posts: 34 Rating: (1) |
I don't understand! Is it working now? |
Best Regards, |
|
12/9/2019 4:26 PM | |
Posts: 12 Rating: (0) |
system is working so isnt problem in configuration, system will stop in above topic.this is my problem. |